Tapping Riser
Alwayslearningelec
NJ
Estimator
Not sure size of existing riser feeding the two panels and I’m getting that info. Have to tap extg. riser( in electrical closet) with new feeder containing 4 #4’s. The basic premise of doing this is you would cut away/intercept section of existing riser pipe, install box for your tap( say above panel) then install new pipe/wire back down to existing panel( which could be gutter tapped)? Obviously also install your new pipe with 4 #4’s from tap box.
is that generally what would need to be done to tap riser? ty
Yes you would cut the existing riser and insert a box, hopefully there is a coupling close by to remove a section of conduit. You would have to change the conductors going in one direction unless you pulled out the existing conductors and pulled them back in.