This has been very helpful. In looking over electrofelons referral to 230.40 it says a service lateral shall supply only ONE set of service entrance conductors, so that would appear to negate the service 'taps' to multiple cabins.
I'm finding the language in 230.40 a bit confusing as to the above. Per the definitions, for underground services, you have:
Utility - Service Lateral (Utility Owned) - Service Point - Underground Service Conductors (Customer Owned) - Service Entrance Conductors.
And the first sentence of 230.40 (omitting the overhead terms) says "Each . . . set of underground service conductors, or service lateral shall supply only one set of service-entrance conductors."
So for the case that you have both a service lateral and one or more sets of underground service conductors supplied by the service lateral, which is it, each set of underground service conductors, or each service lateral?
230.40 aside for the moment, a service lateral could presumably serve multiple sets of underground service conductors, each of which serves one set of service-entrance conductors. Is that allowed under 230.40? Because that is the arrangement you'd have if the CT can is the service point, which is remote both from the pole and from the cabins, and from there you ran individual sets of underground service conductors to each cabin.
I feel like 230.40 is using the phrase "set of underground service conductors or service lateral" to cover the cases where there is only one or the other. I.e. if the service point is on the pole, there's no service lateral, just a set of underground service conductors. While if the service point is at the meter on the building, then there's no underground service conductors, just a service lateral. Which leaves this ambiguity when there is both a service lateral and one or more sets of underground service conductors.
Cheers, Wayne