I don't see why we need "PV disconnects", connecting on the supply some of the "normal" disconnects, etc.
1. Because the service disconnect is the main breaker of a panelboard, and the system can't connect under the 120% rule
2. Because the service disconnect is a breaker that is not suitable for backfeed.
3. Because the PV system is built as a separate service from the service that feeds the building loads, and therefore needs to be line-side of the service meter so it can be on its own service meter. Given hot sequence metering, this would mean you'd have to tie in on the supply side of the service disconnect.
4. Because the site has generator backup and an automatic transfer switch. And in order to avoid a control system to get the inverter and generator to play nicely together, you need to connect on the utility-side conductors of the ATS, so that the PV is off when the generator is running
What we need is a code rule to establish a consensus on what to do about neutral-to-ground bonding in supply-side interconnection disconnects, so this isn't subject to inconsistent opinions of the various AHJ's.