C cppoly Senior Member Location New York Sep 20, 2016 #1 Can you tap transformer secondary conductors or is a fused disconnect required before the tap?
iwire Moderator Staff member Location Massachusetts Sep 20, 2016 #2 cppoly said: Can you tap transformer secondary conductors or is a fused disconnect required before the tap? Click to expand... No, you cannot tap those, they are already taps. But you can run another set of conductors from the transformer terminals to another fused switch.