Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
I have a couple questions: Hypothetical would it be considered a tap connection if you bring in a # 4 AWG SOOW cord with an ampacity of 60 amperes before derating and adjustment into a junction box to be spliced with a “smaller” # 6 AWG nm cable or THHN but rated higher ampacity at 65 amperes before derating at 75 degrees?
Although the larger SOOW cord is feeding the smaller THHN both have an ampacity of 60 amperes or greater. And can be protected by a 60 ampere breaker
Second. Is the ampacity of #4 AWG SOOW cord shown on NEC Table 400.5 rated at 60 or 75 degrees celcius?
I can’t find any reference in NEC to explain what ampacities shown on the table correspond to what temperature?