Taps calculation for Transformer

Status
Not open for further replies.

soldier_sss

Member
Location
trinidad
Hi.

Can someone assist me in calculating the Voltage taps available for the attached transformer.

Thank you.
 

Attachments

  • Trans.jpg
    Trans.jpg
    17.8 KB · Views: 4

templdl

Senior Member
Location
Wisconsin
To

To

Hi.

Can someone assist me in calculating the Voltage taps available for the attached transformer.

Thank you.
How can there be those tap voltages when the primary is 12,000v would be my firrst observation. Strange.
Could you ask GE to look up the S/N and varify that the nameplate is in fact correct. Errors have been know on nameplates where a wrong drawing is used or a typo is made. But what Ii find strange is that the transformer appears to be older and should there be an error how it got by for so long.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
At first glance, looking at the dashed line and associated contact points, I wonder if this is actually showing that the primary is six windings that can be connected in series for 12000V input or in parallel for 6000V input?
If not, then the only possible tap changing would be for one set of windings shown to be many fewer turns than the other allowing for only two different tap positions with the ratio change not shown on the nameplate. Essentially connecting the two windings (per phase) in series or leaving one set disconnected and taking the ouput from the other set only.
Or the dashed line and contacts actually hide the presence of an unspecified number of taps at different turn counts at the end of each of the windings, with the mechanical changing happening through an insulated mechanism to the outside.
If so, it would be an internal tap changer with the tap points not actually leaving the transformer. (Which makes a lot of sense for MV/HV.)

There has to be better documentation than the nameplate available somewhere, even if you have to go back to GE with the serial number.
 

Tony S

Senior Member
In effect you have this

Tap%20Changer_zpswjlvn2th.jpg


Usually in 2.5% increments 12000V being position 3

1 = 11400
2 = 11700
3 = 12000
4 = 12300
5 = 12600
 