Hello all. I am not well-versed in taps. I have a battery charger vendor who has put together a scheme (photo below) for distributing power to a rack full of forklift-style battery chargers. The portion of the drawing above the horizontal line is existing infrastructure, while the lower portion is what they propose to add.
My initial thoughts are:
Am I looking at this correctly in terms of the NEC? Please share any thoughts.
My initial thoughts are:
- Existing infrastructure, now that I examine it closely, is in violation of 240.21(B) (3). The length of #1 AWG from the I-Line panel to the first splitter is over 25 ft. Also 240.21(B) (4) cannot apply since this is not a manufacturing building. Furthermore, there are cases of horizontal conductor length greater than 25 ft, and it also penetrates a ceiling. (There are (6) of these circuits in total).
- The proposal by the battery charger vendor would further introduce taps feeding taps, which I understand is not allowable (though not specifically spelled out in the NEC).
Am I looking at this correctly in terms of the NEC? Please share any thoughts.