I would really appreciate it if someone could verify the following is Code compliant with 240.21(B), and that there is no other pertinent section I could be violating.
I provided a sketch. I hope it is visible.
1. The taps are less than 10 feet
2. Taps are in raceways
3. Taps are 10 AWG (30 A )
4. Taps terminate in 30 A fused disconnects with 30 A fuses
5. The ampacity of each tap (30 A) is not less than 10% of the 150 A primary protection (15 A)
6. The 93 kVA transformer primary protection is set at 150 A (FLA x 133%)
7. This is in an industrial setting
8. The total of the four circuits does not exceed 125% of the FLA of the secondary of the transformer (112 FLA x 1.25 = 140 A)