jeff kurtz
Member
I've got a building(the chapel on a college campus where I work) which was upgraded a few years ago and the entire electrical system was pretty much replaced. The feed is 480V, 3-phase which goes to a 400-amp fused disconnect, then to a 300 kva step-down transformer, to a distribution panel and out to all the power panels. The step-down transformer steps down from 480 to 120/208. Unfortunately, there are some of the old loads which are 240V single phase which are not served by the new system and are fed from a 75 kva single-phase transformer which is not even in the building.
I don't know if this is legal by code, because if you kill the building's main, you do not shut off all the power going through the building, and some of the 240 Volt circuits are in the same conduit as the building's system branch circuits.
In any event, I'm wondering if I can tap a single-phase circuit off of the load side of the 400-amp fused disconnect which feeds the building's step-down transformer, install another smaller appropriately fused disconnect directly on the side of the 400-amp disconnect,(to protect the 75 kva transformer's primary) with wire sized for the smaller transformer, move the single-phase 75 kva transformer inside the building electrical vault next to the newer 300 kva transformer, then feed the 240V loads.
I did put a clamp-on on the building feed wires and each phase is only drawing about 20 amps and the 240V loads don't add up to more than 20 or 30 amps, so overloading is not an issue.
The main on the 240V power panel which is now being fed from the 75 kva transformer is sized at 125 Amps.
My objective is to have a building main which does shut off all power to the buildings.
Is what I'm proposing advisable, legal, and necessary?
Incidentally, I think what happened was an oversite on the part of the EC, not realizing there were 240 V loads because the breaker which feeds the 75 kva transformer is labelled "temp. power", the power panel which feeds the 240V loads is behind the 300 kva transformer and not at all accessible, and there is no mention of it on the remodel prints. I also plan to move the power panel which feeds the 240V loads to a more appropriate location.
I don't know if this is legal by code, because if you kill the building's main, you do not shut off all the power going through the building, and some of the 240 Volt circuits are in the same conduit as the building's system branch circuits.
In any event, I'm wondering if I can tap a single-phase circuit off of the load side of the 400-amp fused disconnect which feeds the building's step-down transformer, install another smaller appropriately fused disconnect directly on the side of the 400-amp disconnect,(to protect the 75 kva transformer's primary) with wire sized for the smaller transformer, move the single-phase 75 kva transformer inside the building electrical vault next to the newer 300 kva transformer, then feed the 240V loads.
I did put a clamp-on on the building feed wires and each phase is only drawing about 20 amps and the 240V loads don't add up to more than 20 or 30 amps, so overloading is not an issue.
The main on the 240V power panel which is now being fed from the 75 kva transformer is sized at 125 Amps.
My objective is to have a building main which does shut off all power to the buildings.
Is what I'm proposing advisable, legal, and necessary?
Incidentally, I think what happened was an oversite on the part of the EC, not realizing there were 240 V loads because the breaker which feeds the 75 kva transformer is labelled "temp. power", the power panel which feeds the 240V loads is behind the 300 kva transformer and not at all accessible, and there is no mention of it on the remodel prints. I also plan to move the power panel which feeds the 240V loads to a more appropriate location.