Would anyone mind trying to explain to me why these parts of the "tap" rules are necessary? Are you allowed to use wiring methods that are not allowed to be exposed to physical damage without providing some kind of additional approved physical protection?
Thanks
240.21(A) (2017)
(1) (10')
(2) (<25')
(3) (25')
(4) (>25')
(5) (Outside)
Thanks
240.21(A) (2017)
(1) (10')
(3) Except at the point of connection to the feeder, the tap conductors are enclosed in a raceway, which extends from the tap to the enclosure of an enclosed switchboard, switchgear, a panelboard, or control devices, or to the back of an open switchboard.
(2) (<25')
(3) The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
(3) (25')
(4) The primary and secondary conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
(4) (>25')
(5) The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
(5) (Outside)
(1) The tap conductors are protected from physical damage in an approved manner.