I have incoming service conductors 4 sets of 600 kcmil to 1600 amps service disconnect.
The load side of service disconnect 4 sets of 600 kcmil feeds trough from which they are tapped to five disconnects for five different tenants all less than 10 feet from the trough.
First disconnect: 4#3/0 Awg and #6 Awg ground tapped to 200A disconnect.
Other three disconnects: 2 sets of 3/0awg and #3 Awg ground tapped to 400A disconnects.
I read somewhere parallel feeders have to be terminated at both ends but not sure about above case. Since I have parallel feeders which are tapped, would the above be allowed per code?