Seeing no such language in 430.1 in the 2017, 2020, or 2023 NEC. Is that a typo?Does anyone know why 430.1 part refers to motor feeder taps as being no less than the feeder ampacity.
Sorry that was a typo on my part it is 430.28. Under the third requirement it states the have an ampacity not less than the feeder conductorSeeing no such language in 430.1 in the 2017, 2020, or 2023 NEC. Is that a typo?
430.28 does say "Feeder tap conductors shall have an ampacity not less than that required by Part II." But that's just a reiteration of the idea that any conductor must have an ampacity at least equal to the load served. It doesn't refer to the ampacity of the feeder being tapped.
Cheers, Wayne
Read a little more carefully. It does not say you have to meet #3, but rather Item 1, 2 or 3.Sorry that was a typo on my part it is 430.28. Under the third requirement it states the have an ampacity not less than the feeder conductor
Re read what i wrote obviously you didn’t understandRead a little more carefully. It does not say you have to meet #3, but rather Item 1, 2 or 3.
Of course its a feeder tap . A motor feeder tap thats the whole purpose of this thread. Why is this a tap when using requirement 3 yet a regular non motor tap is slightly different rulesIf you like, change 430.28(3) to read "Have an ampacity not less than the feeder conductors (in which case it won't be a feeder tap)."
Cheers, Wayne
The upshot of choice (3) in 430.28 is that you don't have a feeder tap. It's just a roundabout way of saying "if your ampacity is too low, you have to comply with (1) or (2)."Of course its a feeder tap
I look at if the wire is the same size/ type for ampacity it's an extension of the feeder it's self. So there would not be a length rule that applies to the splice (tap) location.Of course its a feeder tap . A motor feeder tap thats the whole purpose of this thread. Why is this a tap when using requirement 3 yet a regular non motor tap is slightly different rules
This has nothing to do with the questionI think 240.21 (10% and 30%) are based on the overcurrent device and since motors and motor overcurrent/GF devices aren't always sized the same, in 450.28 they base it on feeder conductor ampacity.
This is exactly what i was getting atWe shouldn't necessarily assume that the 240 definition of a tap applies here, so 'tap' may have the less formal meaning here. In any case, 430.28 basically just repeats some of the rules in 240.21. I don't know why it shouldn't just consist of a reference to the same.
That wasnt the questionI look at if the wire is the same size/ type for ampacity it's an extension of the feeder it's self. So there would not be a length rule that applies to the splice (tap) location.
I think 240.21 (10% and 30%) are based on the overcurrent device and since motors and motor overcurrent/GF devices aren't always sized the same, in 450.28 they base it on feeder conductor ampacity.
Yes, certainly.Is the feeder overcurrent device allowed to be larger than the feeder ampacity for motors?
It doesn't. Both 240.4 and 240.21 have subsections that reference Article 430 as alternatives to the main rule.Also I don't really understand how Chapter 4 can modify Chapter 2 here.
Yes, certainly.
So if 'tap' is not meant in the formal 240.21 sense, then (3) is just another option for meeting the required ampacity of the tap.This is exactly what i was getting at