080504-1646 EST
Leigh:
I just ran some crude source impedance measurements. Test instruments -- Fluke 27, and a 10.6 ohm resistor (electric heater hot. its room temperature resistance is 8.6 ohms). All my wire is copper. Even to the pole.
Very close to main panel. At most 2.5*2' of #12. Includes main fuses and 1 QO breaker.
No load 123.5 V, loaded 122.5 V. I = 122.5/10.6 = 11.56 A. Voltage change 1 V. Source impedance = 1/11.56 = 0.087 ohms.
Kitchen counter. 30'*2 of #8 and about 25'*2 of #12. Same as above but one additional QO breaker.
No load 122.8 V, loaded 119.7 V. I = 119.7/10.6 = 11.3 A. Voltage change 3.1 V. Source impedance = 3.1/11.3 = 0.27 ohms.
At one of my shop benches. 50'*2 of #8 and about 25'*2 or more of #12 and several plugs. Main fuses, a breaker at main, breaker at first bench, followed by another breaker on second bench.
No load 123.3 V, loaded 116.7 V. I = 116.7/10.6 = 11.0 A. Voltage change 6.6 V. Source impedance = 6.6/11.0 = 0.6 ohms. I expect substantial drop in the several plugs.
My wire lengths and sizes are guesstimates. My service is 200 A.
Can your instrument give you this information directly, if not it can be approximately calculated from your fault current measurements? And do you have any comparable measurements to compare with mine? Almost any locations that would show close to the main panel value and a far away value.
.