rodneee

Senior Member
the building was a small two story, stick frame single family home built in the early 50's...in the early 70's it was converted to a tavern with a small dining area...the new owner will now feature live music in what was the dining area...he is now planning to add a drop ceiling for better sound purposes...we will be adding, replacing and relocating 20 +/- existing ceiling pendant lights to recessed in the drop ceiling...all of the existing lights are wired in romex...very few (if any) of the existing light JB's can be moved...(Ques #1) is it legal for me to add romex jumpers to the the new light locations??...if not i will use MC jumpers...(Ques #2) is it legal to have the existing romex in the same JB as the new MC jumpers??
 

raider1

Senior Member
Staff member
Location
Logan, Utah
...(Ques #1) is it legal for me to add romex jumpers to the the new light locations??...if not i will use MC jumpers...

NM cable is not permitted to be run exposed above a suspended ceiling. (See 334.12(A)(2))

...(Ques #2) is it legal to have the existing romex in the same JB as the new MC jumpers??

There is nothing wrong with NM cable and MC cable installed into the same J-box provided that the MC cable is bonded properly.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the remodel is going to increase the possible occupancy level he may be opening a whole new can of worms consisting of building/fire codes including the possibility of having to comply with NEC Art 517 if the new occupancy level is 100 or more persons.
 

mcclary's electrical

Senior Member
Location
VA
the building was a small two story, stick frame single family home built in the early 50's...in the early 70's it was converted to a tavern with a small dining area...the new owner will now feature live music in what was the dining area...he is now planning to add a drop ceiling for better sound purposes...we will be adding, replacing and relocating 20 +/- existing ceiling pendant lights to recessed in the drop ceiling...all of the existing lights are wired in romex...very few (if any) of the existing light JB's can be moved...(Ques #1) is it legal for me to add romex jumpers to the the new light locations??...if not i will use MC jumpers...(Ques #2) is it legal to have the existing romex in the same JB as the new MC jumpers??




Around here, this would be a "change of use" permit, nothing would grandfather in, so as Chris noted, all the NM that is exposed(above the ceiling or not) would be coming out
 

raider1

Senior Member
Staff member
Location
Logan, Utah
If the remodel is going to increase the possible occupancy level he may be opening a whole new can of worms consisting of building/fire codes including the possibility of having to comply with NEC Art 517 if the new occupancy level is 100 or more persons.

I think you mean Article 518 Assembly Occupancies.

Article 517 is Titled Health Care Facilities.;):)

Chris
 

Article 90.1

Senior Member
Cool! So if a tavern is a health care facility, then I can just leave my $35 copay on the counter, drink all I can, then have the bartender bill my insurance company for the balance, right?
 