When tray cable enters a class 1 division 2 location and converts to ridgid conduit without a fitting, which enters a (terminal box, Motor, control box) is a conduit seal required?
When tray cable enters a class 1 division 2 location and converts to ridgid conduit without a fitting, which enters a (terminal box, Motor, control box) is a conduit seal required?
A seal is not required unless the terminal box, motor or control box is XP rated. A cable gland and a low point drain - in outdoor locations - is required where the cable enters the wireway. If the conduit is NOT used as a wireway but as a support means for the TC cable, eg. the opposite end from the tray is not connected to the served equipment then a pop-on bushing on both ends of the conduit and a cable gland termination of the cable to the served equipment will be appropriate. No low-point drain would be required in the later.