7-81 Log #2701 NEC-P07 Action: Reject
(336.10(7))
_______________________________________________________________________________________________
Submitter: Dorothy Kellogg, American Chemistry Council
Panel Meeting Action: Reject
Panel Statement: TC cables are designed for installation in cable trays. They have nonmetallic outer jackets to facilitate installation without damage to the cabled insulated conductors within. The cables are not designed for exposed installations. A specific construction of TC was developed with enhanced overall cable mechanical performance to
enable the cable to meet the crush and impact requirements of MC cable. The enhanced cable is permitted for specific applications to be installed outside of a cable tray. Expansion of the use of TC beyond those specific applications will expose the cable to damage that it is not designed to withstand. The differences in the physical properties nonmetallic and metallic outer coverings are very different. The tensile strength of steel and aluminum is typically 72,000 and 42,000 psi, respectively. The tensile strength of a nonmetallic covering is typically 2,000 psi. Simply meeting a crush and impact requirement does not encompass the abilities of a metallic outer covering on the cable.