GarwoodV6
Member
- Location
- Houston suburbs
- Occupation
- 30 year commercial Electrician
Cleaning up a Service and feeder on an existing home (built 1972) with 1/0 AL SE bare neutral, no ground feeding between floors to an existing 200A MLO panel located 25 feet across the attached garage from the original 200A Federal Pacific (!) Main breaker (Only) panel located inside garage behind 200A meter socket outside.
I can't believe triplex (bare neutral, no ground, open wire in attic and through joists between floors was used as a feeder inside the house, much less 1/0 which is only rated for 125A
Need to get rid of that F-P Main and upgrade the feeder to provide separate ground.
A whole-house generator installer pointed out code violations as well as signs of wire overheating on the existing service to the homeowner, and the owner wants to bring this up to current code for all the right reasons. Copper only, per the homeowner.
Putting an exterior MCB after the new Generator ATS and re-feeding the house with 4-wire feeder rated for 200 amps is the goal. the problem is the feeder route.
I need a Clarification:
Can TC-ER (marked JP) copper 2/0X3 with #6 ground cable be used as a 200A feeder without conduit inside the attic, between floors and down an interior wall?
It appears so, according to NEC 330.10 (9)
It also appears that it can be run on joists and through the wall top plate, secured every 4-1/2 feet etc. as in NM.
A crawl space alongside the 2nd floor will get me from the new outdoor 200A MB feed-through panel, but the panel is ~4-5 feet under the 2nd floor.
I can go around side of 2nd floor, chase the cable between 2nd floor joists from the crawl space and down into the interior wall where the existing home panel is now.
Crawl space access is very limited, and pipe run between floors would require a lot of demolition.
2/0 SER has a vastly oversized #1 ground, is unbelievably stiff, and is quite a bit more expensive than TC-ER "JP". I don't think I could man-handle the SER into place under these conditions. The TC-ER should be more manageable.
I can't believe triplex (bare neutral, no ground, open wire in attic and through joists between floors was used as a feeder inside the house, much less 1/0 which is only rated for 125A
Need to get rid of that F-P Main and upgrade the feeder to provide separate ground.
A whole-house generator installer pointed out code violations as well as signs of wire overheating on the existing service to the homeowner, and the owner wants to bring this up to current code for all the right reasons. Copper only, per the homeowner.
Putting an exterior MCB after the new Generator ATS and re-feeding the house with 4-wire feeder rated for 200 amps is the goal. the problem is the feeder route.
I need a Clarification:
Can TC-ER (marked JP) copper 2/0X3 with #6 ground cable be used as a 200A feeder without conduit inside the attic, between floors and down an interior wall?
It appears so, according to NEC 330.10 (9)
It also appears that it can be run on joists and through the wall top plate, secured every 4-1/2 feet etc. as in NM.
A crawl space alongside the 2nd floor will get me from the new outdoor 200A MB feed-through panel, but the panel is ~4-5 feet under the 2nd floor.
I can go around side of 2nd floor, chase the cable between 2nd floor joists from the crawl space and down into the interior wall where the existing home panel is now.
Crawl space access is very limited, and pipe run between floors would require a lot of demolition.
2/0 SER has a vastly oversized #1 ground, is unbelievably stiff, and is quite a bit more expensive than TC-ER "JP". I don't think I could man-handle the SER into place under these conditions. The TC-ER should be more manageable.