TC-ER-JP cord -

Status
Not open for further replies.
Other wise known as Tray cable. But, this cable is special - made by Honeywell it's a product on the market called "Genesis P/N 1070-14 AWG 4/C THWN-2 / THHN CONDUCTORS MINI SPLIT 12517 (UL) TC-ER-JP DIRECT BURIAL SUN RES (RoHS). - which is screen printed on the cord.
Its specifically designed for use with mini split AC units. It looks like it has all the properties that one would want to use for the application. However, the outdoor unit I inspected was on a roof top of a commercial building in one of the five boroughs in NYC. So all is well and good - supported - kinda with tie wraps to the seal tite. But, here's my issue the TC cord penetrated the roof and was routed "concealed" through the ceiling in route to the indoor unit. TC cable is covered in Article 336 of the NEC but I dont see anything about it being concealed. Does it fall under the do's and dont's of Article 400 ?

Is this in compliance? Please help. Thanks
 
Sounds like the installer made a mistake, I think it needs to be in a tray or raceway unless its in a one or two-family dwelling unit.
2017 NEC 336.10(9)
Code:
 In one- and two-family dwelling units, Type TC-ER cable
containing both power and control conductors that is iden-
tified for pulling through structural members shall be
permitted. Type TC-ER cable used as interior wiring shall
be installed per the requirements of Part II of Article 334.
 