TCC Curve for Circuit Breaker

Grouch1980

Senior Member
Location
New York, NY
I've searched and searched through Google, but cannot find the TCC curve for a Siemens Q3100 circuit breaker. It's a 3 pole, 100 amp circuit breaker. Can someone please help? :)
 

lielec11

Senior Member
Location
Charlotte, NC
SKM has two versions, one labelled as Rev. 4, one as Rev. 6. I'm assuming it might be related to when the breaker was manufactured but I'm not certain. Both are on the attached file for reference.
 

Attachments

  • Form - TCC & One-Line 8 1.pdf
    151.2 KB · Views: 12

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
So I just extend the instantanous region on the right all the way out to 22k?
No.

The AIC rating does not affect the TCC at all.
The AIC is about the protective device not turning into shrapnel while it is clearing a fault.

You should always extend your instantaneous region up to the fault current 'flowing through' the protective device.
 

Grouch1980

Senior Member
Location
New York, NY
Hmm. I was under the impression the right most line on a circuit breaker graph is its AIC rating. So if the rating is 65k, that right most line (the vertical boundary) will be at 65k.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Hmm. I was under the impression the right most line on a circuit breaker graph is its AIC rating. So if the rating is 65k, that right most line (the vertical boundary) will be at 65k.
Not always.
The AIC point might be where the curve 'ends', but many different AIC ratings may actually share the same TCC.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
All of the Siemens TCCs for the QP breakers are the same regardless of size.

Finding them on Siemens website is challenging though. I found them in the past, can’t any more.
 

lielec11

Senior Member
Location
Charlotte, NC
Hmm. I was under the impression the right most line on a circuit breaker graph is its AIC rating. So if the rating is 65k, that right most line (the vertical boundary) will be at 65k.
The right (or top) most lines are the actual clearing time of the breaker or fuse. For a fuse, the left/bottom lines are when the fuse actually starts melting, and the right/top is where it fully clears the fault.

For breakers, the left/bottom is where the device physically starts to unlatch/open, and the right/top are where the breaker is actually open and clears the fault.
 