lielec11
Senior Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer (PE)
I am having a hard time trying to protect a transformer properly using SKM. In the image below, the primary side protection (fuse "PD-0001") should be to the right of the inrush point at the bottom and then to the left of the primary side damage curve at the top. However, no matter what fuse I choose in the SKM library, none of them achieves both of these principals. In fact, I cannot even get close. I am sizing my fuse based on 125%. Am I missing something here? Test project parameters are below for your reference, any help or input is greatly appreciated.
1000kVA Dry Type Transformer
480V Delta - 208Y/120V
PD0001: Gould Shawmut A4BT 600V, 600A fuse
PD0002: Cutler Hammer DSLII-840 4000A circuit breaker

1000kVA Dry Type Transformer
480V Delta - 208Y/120V
PD0001: Gould Shawmut A4BT 600V, 600A fuse
PD0002: Cutler Hammer DSLII-840 4000A circuit breaker