Perhaps my addled brain is missing it, but I don't see how to program this VFD to trip off at a programmed overload level. We're using it to drive an art display and want it to just stop if someone drops trash or junk in the works and jams the mechanism.

IIRC it has a 1/2 HP 40:1 gear-motor running at about 7 Hz. If I jam the mechanism the motor does stall, but I'd like it to stop. (I haven't yet measured the run current, but it's got to be close to nothing, doing that tomorrow.)

If someone can point me to the correct register, I'd be grateful.
 
08-05 is where you program the OL action, i.e. whether you want it to trip, then if you want a different trip time for cold or hot start. Basically, it trips at 150% of rated current in 3.5 minutes for hot start, or 5.5 minutes for cold start.

You can't set the level of trip current directly, you can only set the Motor Rated (nameplate) Current, in 02-01. So if you want it to trip at less current, you will have to "lie" to the drive as to the motor FLA setting.

A lot of VFDs will provide a SEPARATE trip point for something like "Jam" protection, or "Electronic Shear P{in", but this drive does not have anything like that. You only have the OL protection.
 
@Jraef Thanks for that, makes sense (lie to the controller :LOL:), one of my coworkers though it had some sort of jam protection. With the (lack of) rolling resistance of the piece, I suspect the OL setting will be rather low, so we may just let things go. (I have all weekend to try things....).

@ptonsparky For the next one I may look at using some sort of a movement detector/teeth counter, but also at a VFD with jam protection. Or get the designers to include some sort of a slip clutch/torque limiter.
 