Can i use TEFC Motor in Class 1 Division 2 areas as per NEC standards
Y yanno New member Oct 20, 2003 #1 Can i use TEFC Motor in Class 1 Division 2 areas as per NEC standards
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 20, 2003 #2 Re: TEFC Motor Maybe. See 501.8(B). As long as the motor has no arc producing contacts of any type, you can use the TEFC motor in a Class 1 Div 2 area. Don
Re: TEFC Motor Maybe. See 501.8(B). As long as the motor has no arc producing contacts of any type, you can use the TEFC motor in a Class 1 Div 2 area. Don