I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?
I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.
I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.
I think in the case of Cl. I, Div. 1 environment I would be more concerned with the Teflon tape ALTERING the explosion relief capability of the connection than the grounding continuity. (Not that it is not important, but it would be secondary.)
250.96 Bonding Other Enclosures.
(A) General. Metal raceways, cable trays, cable armor, cable
sheath, enclosures, frames, fittings, and other metal non–
current-carrying parts that are to serve as grounding conductors,
with or without the use of supplementary equipment
grounding conductors, shall be effectively bonded where necessary
to ensure electrical continuity and the capacity to conduct
safely any fault current likely to be imposed on them.
Any nonconductive paint, enamel, or similar coating shall be
removed at threads, contact points, and contact surfaces or be
connected by means of fittings
One would think the explosion relief issue would only come into play with covers of XP boxes, not conduit fittings.
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?
there is a product called led-plate, which is similar to kopr-shield, with lead
instead of copper. it's used a lot in the refineries in cl 1 div 1 occupancies.
just a messy anti-sieze that is electrically conductive, and works on a number
of things.... really bad on carpeting if you get some on the bottom of a shoe.
a spoonful will cover a football field, with some to spare. :smile:
One would think the explosion relief issue would only come into play with covers of XP boxes, not conduit fittings.