help me with this ? We got a piece of equipment in for class 1 div1 and all of the fittings and seals have teflon tape?! I think it all need to be removed per 250.96 and 250.100 , what do you think
 
Teflon tape does not prevent bonding. It basically just fills in the air gaps on the threads. I am not sure this is a violation. I am not sure it isn't a violation either.
 
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?
 
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?
I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.
 
I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.

I think in the case of Cl. I, Div. 1 environment I would be more concerned with the Teflon tape ALTERING the explosion relief capability of the connection than the grounding continuity. (Not that it is not important, but it would be secondary.)
 
I have no idea Don; I do know any treatment of the bonding path better enhance it rather than just not interfere with it in classified locations. That is the emphasis in 501.30(A) which applies to both Division 1 & 2. However, the OP cited sufficient Code in 250.96 alone to justify removing the Teflon.

I don't see how those paragraphs say anything of the sort. Perhaps you could enlighten me as to what wording prohibits teflon tape.
 
Last edited:
I think in the case of Cl. I, Div. 1 environment I would be more concerned with the Teflon tape ALTERING the explosion relief capability of the connection than the grounding continuity. (Not that it is not important, but it would be secondary.)

One would think the explosion relief issue would only come into play with covers of XP boxes, not conduit fittings.

250.96 Bonding Other Enclosures.
(A) General. Metal raceways, cable trays, cable armor, cable
sheath, enclosures, frames, fittings, and other metal non–
current-carrying parts that are to serve as grounding conductors,
with or without the use of supplementary equipment
grounding conductors, shall be effectively bonded where necessary
to ensure electrical continuity and the capacity to conduct
safely any fault current likely to be imposed on them.
Any nonconductive paint, enamel, or similar coating shall be
removed at threads, contact points, and contact surfaces or be
connected by means of fittings

It seems to me you have a choice. I don't see how teflon tape is all that similar to paint in any case.
 
Last edited:
If it could even possibly affect the bonding path, it violates 501.30(A). If it coats the thread at all with a nonconductive material (that's how it is similar), it violates 250.96.
 
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?

Anti-seize/never-seize? It's conductive, typically nickel or copper based, and is functionally the same as a thread lubricant.
 
The rule reads 4.5 for an exception. (05 Nec) 500.8(D) Ex.

Standard is about six to seven.

Teflon tape? Needs to go away.

C1D1 piping is all about limiting flame propagation and expansion, from within, or from outside the pipe, box etc. Threading is based upon allowing the gasses time enough to cool in travelling the distance involved. That is why we use tapered threads, and thread lube (kopr shield) to enhance grounding by reducing corrosion of the base metal (the pipe). Look at the lips of an explosion proof box. There is a reason they are that thick, and can cost thousands of dollars to purchase.
 
See the 2008 HB, last paragraph in the commentary.

"The use of Teflon tapes or joint compounds on conduit threads may weaken the seal fitting and interrupt the equipment grounding path. Cracks have developed in fittings during hydrostatic testing in which these materials were used."

My humble opinion. If you received equipment from a skid manufacture that has teflon tape on the conduit threads it means it was fabricated by pipe fitters or plumbers, not qualified electricians. Better make sure your fittings are all conduit fittings and verfiy there are no black iron pipe fittings mixed in.

I have seen it happen.
 
Kudos to all the responders that pointed out the potential of significantly altered explosion relief characteristics. I have long been aware of the grounding issue, but never gave the relief issue any real thought – although it is obvious once it is considered.

Some Ol’ dogs can still learn a thing or two - thanks :)
 
What is permitted to be used on conduit threads? Are there products other than Crouse's STL, Burndy's Penetrox E, or T&B's Kopr-Shield that can be used?

there is a product called led-plate, which is similar to kopr-shield, with lead
instead of copper. it's used a lot in the refineries in cl 1 div 1 occupancies.
just a messy anti-sieze that is electrically conductive, and works on a number
of things.... really bad on carpeting if you get some on the bottom of a shoe.
a spoonful will cover a football field, with some to spare. :smile:
 
there is a product called led-plate, which is similar to kopr-shield, with lead
instead of copper. it's used a lot in the refineries in cl 1 div 1 occupancies.
just a messy anti-sieze that is electrically conductive, and works on a number
of things.... really bad on carpeting if you get some on the bottom of a shoe.
a spoonful will cover a football field, with some to spare. :smile:

Is that the red junk that gets really hard after 40 years? My guys had a heck of a time changing stanchion mount lighting tophats recently that had some sort of red junk on the threads.
 
One would think the explosion relief issue would only come into play with covers of XP boxes, not conduit fittings.

I can't remember if it was an OZ-G or Appleton catalog, but it showed at the fittings the threads are considered an explosion exhaust component, allowing the gas to cool and exit without being an ignition source.
 