Tele/datacomm wiring ran through ventilation ducts

Status
Not open for further replies.

motownguy

Member
Hi Mike I am writing you in regards to some Cat-5-e cabling Ran through many of the older schools Air ducts through out the city of Detroit.
I Feel that in the event of a fire the cabling with in the ducts in the older schools will pump the fumes through class rooms and even the plenium rated CMP cable still will burn.
What code can I referance the installing contractors. Brian
Brian.flynn@detroitk12.org :confused:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Tele/datacomm wiring ran through ventilation ducts

Brian,
800.51(A) appears to permit the use of plenum rated cables in ducts provides that it is also listed as having adequate fire-resistant and low smoke-producing characteristics.
Don
 

robert

Member
Location
Michigan
Re: Tele/datacomm wiring ran through ventilation ducts

Check out 800-53 (a) out of the 99 code book. Seems to me that people do what they want with communication and get away with it.
 