Hey guys,
I have a 2nd Floor IDF room that has a telecom ground bar (TGB). The racks are bonded to it, however, the contractor did not install the #6 bonding conductor that is supposed to go from the TGB to the main service ground bar in the 1st floor elec room which thus is tied to the grounding electrode system.
Instead, he just runs a bonding conductor from the TGB to a nearby panelboard's equipment grounding bus inside the panel. Is that a code violation? I know its not good practice to mix telecomm grounds and electrical grounds until you are at the main elec service room where they all tie together.
Building is now finished and contractor is concerned about routing new bonding wire all the way back to elec room. Trying to find an alternate solution...
Thanks,
I have a 2nd Floor IDF room that has a telecom ground bar (TGB). The racks are bonded to it, however, the contractor did not install the #6 bonding conductor that is supposed to go from the TGB to the main service ground bar in the 1st floor elec room which thus is tied to the grounding electrode system.