Hi friends,
There is a factory manufacturing telecommunication equipment such as TV TX/RX or mobile cells. Do you think that the following grounding scheme would be resonable for such a premise (double-floor, more than 1000 square meter area, and fed by a 20kV/380v delta/star)?
- grounding electrode system:
#4 earth well connected in a star manner to the service panel grounding bar, which is bonded to the neutral bar and, also, the structural steelwork and piping as well (overal resistance less than 4 ohm). Distance between transformer frame ground electrode and building grounding electrode system is less than 20 meters, Doesn't it poses any danger? Isn't a ground ring around the building necessary?
- equipment grounding:
The equipment signal reference (on printed board) is bonded to the equipment chasis/enclosure and to the safety equipment grounding conductor (EGC), i.e. a common safety/signal EGC. All the insulated EGCs are routed in a star manner down to the service panel ground bar (single point grounding). Anyway, when testing equipment, there is a ground loop between equipment and instrument. To resolve that, is it reasonable to feed both items from a common AC receptacle and swap the feeding cords up to them?
Equipment work at MHz Range.
Any advise or comment is highly appreciated ...
There is a factory manufacturing telecommunication equipment such as TV TX/RX or mobile cells. Do you think that the following grounding scheme would be resonable for such a premise (double-floor, more than 1000 square meter area, and fed by a 20kV/380v delta/star)?
- grounding electrode system:
#4 earth well connected in a star manner to the service panel grounding bar, which is bonded to the neutral bar and, also, the structural steelwork and piping as well (overal resistance less than 4 ohm). Distance between transformer frame ground electrode and building grounding electrode system is less than 20 meters, Doesn't it poses any danger? Isn't a ground ring around the building necessary?
- equipment grounding:
The equipment signal reference (on printed board) is bonded to the equipment chasis/enclosure and to the safety equipment grounding conductor (EGC), i.e. a common safety/signal EGC. All the insulated EGCs are routed in a star manner down to the service panel ground bar (single point grounding). Anyway, when testing equipment, there is a ground loop between equipment and instrument. To resolve that, is it reasonable to feed both items from a common AC receptacle and swap the feeding cords up to them?
Equipment work at MHz Range.
Any advise or comment is highly appreciated ...