Telescoping Bleachers Disconnect

Status
Not open for further replies.

Sparky2791

Senior Member
Location
Northeast, PA
Occupation
Electrical Design
I have a project where telescoping bleachers will be used. Manufacturer's engineering department said on the phone they just need a junction box to tie into, a knife switch disconnect is not required. It is a 3 phase circuit, 4 wire, they need the neutral. Their control box holds the thermal overloads and control for the motor which is a 1/2 HP motor. Typically I would just add a disconnect and be done with it but in this case I would have to install it behind the bleachers making it not readily accessible. I cannot install to the side of the bleachers for other reasons.

Does it need a disconnect? I thought I read something in the NEC about fractional HP motors not requiring a disconnect switch.

The panel is not within sight of the bleachers.

Thanks for the reply's!
 
The motor disconnect rules are in 430.102 and are straightforward. Every motor, even a bath ceiling fan requires a disconnect. There is normally a disconnect within sight of the motor and disconnect.
 
The motor disconnect rules are in 430.102 and are straightforward. Every motor, even a bath ceiling fan requires a disconnect. There is normally a disconnect within sight of the motor and disconnect.
Got it. Just FYI - the section I was thinking about, which does not apply to my application due to my HP, is 430.109(B).
 
I have a project where telescoping bleachers will be used. Manufacturer's engineering department said on the phone they just need a junction box to tie into, a knife switch disconnect is not required. It is a 3 phase circuit, 4 wire, they need the neutral. Their control box holds the thermal overloads and control for the motor which is a 1/2 HP motor. Typically I would just add a disconnect and be done with it but in this case I would have to install it behind the bleachers making it not readily accessible. I cannot install to the side of the bleachers for other reasons.

Does it need a disconnect? I thought I read something in the NEC about fractional HP motors not requiring a disconnect switch.

The panel is not within sight of the bleachers.

Thanks for the reply's!
Can't you just use a 3 pole motor rated switch instead of a NF disco? Or, worst case, use a lock off device on the breaker.
 
Don't forget the requirements of 430.102(A) for the controller. It sounds as if you will need a disconnect in sight from the controller.

(Maybe not Code but it sure seems reasonable to have an in-sight disconnect on moving bleachers)
 
Can't you just use a 3 pole motor rated switch instead of a NF disco? Or, worst case, use a lock off device on the breaker.
Sure could use a motor rated switch. Not sure a lock off device would comply with NEC disconnect requirements. Has to be within site and if it is no need for the lock off.
 
The motor disconnect rules are in 430.102 and are straightforward. Every motor, even a bath ceiling fan requires a disconnect. There is normally a disconnect within sight of the motor and disconnect.
Look at exception #3. As long as the device is lockable, it is not required to be within site. I have never seen, designed or installed a disconnect on telescoping bleachers ever and have just put a lockable device on the breaker.
 
Exception 3 is for a vam (2017). I was commenting a disconnect is required for the motor. Often one disco can be used for motor and controller
 