What type cable is not suitable for temporary feeders on a construction?
a) S
b)SJ
c)PD
d)G
a) S
b)SJ
c)PD
d)G
PDWhat type cable is not suitable for temporary feeders on a construction?
a) S
b)SJ
c)PD
d)G
Yes, and yes...Do you know why PD is the answer? If you do, wouldn't you think it might be a good idea to point the student to where he/she can find the answer instead of just giving it to them?
Roger
The answer to the OP question can be determined by first going to 590.4(B) for feeders of temporary installation. It states that cable types must identified for hard or extra-hard usage in Table 400.4. Of the choices available in the question, Table 400.4 lists Type PD as the only one not so identified.