Temp. derating, adjustment, correction factors.

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi
Commercial inspector wants us
to show calc. for roof mounted 200A feeder of air condition sub panel with total load of 110A
.
feeder: 2" EMT, (3) 3/0 THHN, Cu + EQ.GR (off a 75 deg. terminal , 200A/3p cir. breaker)

if it was a more than three hot conductors, then I would calculate so;

200A x .75 (per 310.16) = 150A
i am still fine, no need to increase the conductor size.

What do you think??

Thank you
 

Toros

Senior Member
Location
Tujunga, CA
How did you arrive at .75? Roof adder for temp.

Assuming you used charts:
What ambient temp did you use? What height off roof is conduit?

I have (3) #3/0 copper wire plus EQ.GD
in a 2" EMT 140' long feeding a sub panel used for AC units (with total load of 140A)
@ Temp. of 123-131 (F) in Los Angeles, valley

conduit run across the roof elevated; 1" through red woods
 

jumper

Senior Member
I have (3) #3/0 copper wire plus EQ.GD
in a 2" EMT 140' long feeding a sub panel used for AC units (with total load of 140A)
@ Temp. of 123-131 (F) in Los Angeles, valley

conduit run across the roof elevated; 1" through red woods

If you are only 1” above the roof you have to add 40F more. That puts you at .5 instead of .76.

This whole roof adder thing got deleted in the 2017.

Why is the load now 140A and not 110A?
 

Toros

Senior Member
Location
Tujunga, CA
If you are only 1” above the roof you have to add 40F more. That puts you at .5 instead of .76.

This whole roof adder thing got deleted in the 2017.

Why is the load now 140A and not 110A?

ok
tanx jumper
the chart says correction factors based on more than three conductors
mine is three- hot conductor feeder
how is that....??????
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What code cycle are you under? For the 2017 if you're 1" above the roof there is no adder. Under the 2014 NEC if you use XHHW there is no adder either.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I assume you are using 90C wire so you can de-rate from 225 amps value of the 90C column. As long as the final overcurrent protective device is not larger than 200 or whatever the temp. rating is after de-rating. Start at 225 not 200 amps
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I assume you are using 90C wire so you can de-rate from 225 amps value of the 90C column. As long as the final overcurrent protective device is not larger than 200 or whatever the temp. rating is after de-rating. Start at 225 not 200 amps

Since this is feeding 4 AC units the OCPD can be larger than the conductor size if they used just a feeder but since there is a sub-panel at the end I agree with you.

So assuming that the feeder is the correct size for the load the only issue is do the #3/0 conductors have an ampacity of 200 amps after adjustment.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
How can you have a feeder without a panel?

I believe he can take the largest motor and calculate the largest breaker allowed for that motor and then add the fla of the other motors. Not enough info given...

430.62 Rating or Setting — Motor Load.
(A) Specific Load. A feeder supplying a specific fixed motor
load(s) and consisting of conductor sizes based on 430.24 shall
be provided with a protective device having a rating or setting
not greater than the largest rating or setting of the branchcircuit
short-circuit and ground-fault protective device for any
motor supplied by the feeder [based on the maximum permitted
value for the specific type of a protective device in accordance
with 430.52, or 440.22(A) for hermetic refrigerant motorcompressors],
plus the sum of the full-load currents of the
other motors of the group.
Where the same rating or setting of the branch-circuit shortcircuit
and ground-fault protective device is used on two or
more of the branch circuits supplied by the feeder, one of the
protective devices shall be considered the largest for the above
calculations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How can you have a feeder without a panel?

You run a feeder and tap off to a disconnect for each AC unit. Common practice for AC units and motors.

I never would have thought to do that. You then have to follow tap rules.
 
Last edited by a moderator:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
yes, but I don't see why that should make any difference other then the panel is simpler to add more load to if it still has open spaces.


Can the feeder for multiple units or motors have an OCPD larger than the feeder conductor ampacity to compensate for starting current?
 
Status
Not open for further replies.
Top