Hi
Commercial inspector wants us
to show calc. for roof mounted 200A feeder of air condition sub panel with total load of 110A
.
feeder: 2" EMT, (3) 3/0 THHN, Cu + EQ.GR (off a 75 deg. terminal , 200A/3p cir. breaker)
if it was a more than three hot conductors, then I would calculate so;
200A x .75 (per 310.16) = 150A
i am still fine, no need to increase the conductor size.
What do you think??
Thank you