brantmacga
Señor Member
- Georgia
- Former Child
I have a building being 75% gutted and remodeled.
In a corner of this building is a server room that must stay operational. The existing feeder must be removed and re-worked. The scheduling is going to require me to temp the 60A 208/120v feeder to the panel in this room for at least a month.
I put money in the job for a generator, but looking at the site today, I have concerns about the amount of pedestrian and vehicular traffic around the building. I feel like at some point, it's going to be vandalized. The location isn't as secure as I thought it would be.
I'd like to run a temporary feeder from the existing MDP that will be untouched approx 200' across the building. But every room it passes through will be demo'd.
Is it acceptable to run either an SO or MC cable across the floor to feed this panel? I think there is also the possibility that I can get through the ceiling of the mechanical room and up over the 2nd floor and run it across the bar joists. The main issue with that routing is that the 2nd floor over the mechanical room is not being remodeled, so I would have to get between the floors and into the area being gutted before I can turn up.
I can't start running the conduit for the new feeder until demo is complete.
In the space that is being remodeled, they are completely removing the 2nd floor to make one large area with 19' ceilings.