Temp generator cable

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
I'm looking to temporarily hook-up a trailer-mounted 3-phase generator to an equipment shed with an existing ATS. The genset is selectable voltage, 25kVA, breakered at 60A. It would be slick if I could get cable that would have the power conductors and 2 control conductors for the ATS-automatic start. I know they make that kind of thing for 1-phase residential setups but haven't seen anything for 3-phase setups. Does anyone know of such a thing?
Otherwise, I'm thinking of using some 6/5 Type W cable and a separate piece of ~14/2 SO or SJ for the starting. I've seen some discussions about using Type G cable for this kind of thing, but I don't see the advantage. Thoughts?
Also, would the neutral be a CCC in this scenario? I don't think so but could be corrected. Maybe I could use #8 (57A)?
 
The genset has a removable N-G bond. The ATS is 3-pole (solid neutral).

Am I reading Table 400.5(A)(2) correctly for Type W cable:

75° Column F (3- or other multiconductor cables with only 3 CCC)
8AWG --> 57A
 
As to the cable size, the generator is likely rated at 60.1 amps, with a 60.0 amp breaker that would lead you to 6AWG but if your load is under 57 amps then next-size-up would lead you to 8AWG

As to the G vs W, in the larger sizes type G is usually substantially cheaper but I just looked and a #8 the type W is cheaper plus you don't have to mess with all the individual ground wires.

As to the N-G bond, yes the proper way would be to remove it and ground the generator back to the main bond like any permanent non SDS generator.

Then use whatever cable makes sense for the 2-wire start.
 
I can't show you something that isn't there, but virtually every trailer-mounted generator (maybe 50-250kva) I've touched did not have an N/G bond; I had to add it when needed.

The point is: don't assume, check.
Don’t assume they sent you the right voltage either! I was hooking up a car auction house after a hurricane in Louisiana, they sent one set up for 480 auction place was 208. Changed the taps. Another job the customer sent out the wrong generator, our guys didn’t check it, and just turned it on. Fried the EMS, refrigeration and a lot of other stuff shooting 480 to a 2000 amp 208 volt service.
 