we have a customer which has purchased a 350 kw 120/208 volt 3-phase 4 wire generator, trailer mounted, we expect the generator to have a single
1400 amp breaker factory installed [ and as usual no one has a cut sheet
on the gen-set ] the building in which we intend to connect to has (2)-
services (1)-800 amp & (1)- 600 amp with transfer switches in place, we only
need to extend the existing conduits, & feeders outside to the new 600, & 800 amp enclosed breakers this part we have no questions. we
intend to make the portable camlock cord connections from the gen-set to
the breaker cabinet with parallel 400 amp type16 camlocks & 4/0 600 volt
90-degree cable, is the paralleling of the camlocks & cable (2-sets each)
permisable by the nec.