Not sure how this would be accomplished. So all distribution is existing to remain. So what they are doing in now backing up the ADP and HDP from a standby generator so they are adding ATS’s. We have to remove the feeders and run new feeders from the existing main board to new ATS’s and then the ATS’s will feed the ADP and HDP. They need to have the ADP and HDP live at all times and requested to provide temp generator. My thinking is the temping out would not happen at the main board but at either ADP and HDP( one at a time) so when the feeder serving those panels are removed either ADP or HDP is still live. How would the temp genset cables attached to either ADP or HDP? Right to the bus?
I don’t think the entire main board would need to be shut down in order to move the feeders for wither ADP or HDP. We can just shut that switch down.

Although I'm think the temp genset note implies to temp out the main switchboard which is 3000a.
 