- <font size="2" face="Verdana, Helvetica, sans-serif">We installed an overhead #2 Quadraplex to a pole set next to the Trailer ( about 175' total length). We are supplying 120/240 single phase power to the Trailer Panel. We used 2 insulated conductors for phases, 1 insulated conductor for the neutral, and the bare #2 conductor for the grounding conductor. The source is an existing outdoor weatherproof Dist. center with branch breakers up to 100A single and 3 phase. We treated the Trailer panel as a Sub-Panel, single branch circuit, with an isolated Neutral which originates in the main service Dist. Panel. We attached the Grounding Conductor to the Trailer Panel Buss with a jumper out to the Trailer Frame Ground Lug & at the Dist. Panel Ground Buss. We are now being told that we need to drive a Ground Rod at the Trailer and connect it to our Ground Buss at the Trailer. In this installation without the Ground Rod at the Trailer an NEC Code Violation. Our local inspector opined that it is not, but another local authority has asserted that it is a code violation. We believe that our installation is supported by the following sections of the NEC. 250.32 (A) exception, 500.16 Grounding (Mobil & Manufactured Homes), 500.16 (A)Insulated, 500.16 (B) Electrical System. Is it optional to install this additional Ground Rod ? We have provided a full size Grounding conductor with our feeders. Won't the addition of this Rod create a Ground Loop and an alternate path with different Impedance then the service ground ?</font>