TEMP PANEL

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
These are the new panels with new ckts to extg.loads but I have to temp out the extg. loads which are the following:


DP-1- All ckts except DP-1.
DP-2 all ckts.

Could I get away with one 800A temp panel for ll these loads? Since Im not needing to temp out DP-2 I'm think a ~600a temp panel would suffice and would still need the 225A for the other loads. Thinking one 800A panel would work for all those loads.

What would you use as a tyemp panel for all these loads...one panel, two? Thanks
 

Attachments

  • Capture.jpg
    Capture.jpg
    15.9 KB · Views: 0

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
You have 21 x 3P breakers in DP-1, that's 63 poles. Not more than 42 over current devices can be installed in any one cabinet 408.54.

And a 3 pole breaker counts as 3 OCPD's; which would mean 2 panelboards.
 