Re: temp pole

590.2(A) :)oops, that's 2005. 2002 would be 527.2(A). :)

[ August 25, 2005, 07:30 PM: Message edited by: redfish ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: temp pole

Originally posted by lefty150:
where in the nec 2002 code does it say a temp pole must conform to art. 230
Temp or not it is a service.

230.1 Scope.
This article covers service conductors and equipment for control and protection of services and their installation requirements.
And if we look at 527


527.2 All Wiring Installations.
(A) Other Articles. Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.
 