Guys - I have some temp power skids with a 480v panel on one side and the main breaker is about 7' 5" AFG - does the max breaker height apply to Temp power set ups?(6'7")
This section is often overlooked where temporary power is being installed.
590.2 All Wiring Installations. (A) Other Articles. Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.