A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?That section in the 2020 prohibits the use of the MLO panels with multiple service disconnects in the panel.
That should be fine.A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?
You don't even need a hold down. Nothing in that new code prohibits a single breaker (single handle) in a MLO panel.A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?
What about 408.36(D)?You don't even need a hold down. Nothing in that new code prohibits a single breaker (single handle) in a MLO panel.
Yes just land on the MLO lugs. MLO service panels aren't prohibited, just having more than one handle installed in them is. There is 230.62, but those don't have to be manufacturer provided.What about 408.36(D)?
Or are you suggesting that the service conductors land on the MLO lugs?
Then what serves as a main disconnect?Yes just land on the MLO lugs. MLO service panels aren't prohibited, just having more than one handle installed in them is. There is 230.62, but those don't have to be manufacturer provided.