A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?That section in the 2020 prohibits the use of the MLO panels with multiple service disconnects in the panel.
That should be fine.A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?
You don't even need a hold down. Nothing in that new code prohibits a single breaker (single handle) in a MLO panel.A 2 pole circuit breaker with a hold down device and protective covers over the line side lugs would meet the requirement?
What about 408.36(D)?You don't even need a hold down. Nothing in that new code prohibits a single breaker (single handle) in a MLO panel.
Yes just land on the MLO lugs. MLO service panels aren't prohibited, just having more than one handle installed in them is. There is 230.62, but those don't have to be manufacturer provided.What about 408.36(D)?
Or are you suggesting that the service conductors land on the MLO lugs?
Then what serves as a main disconnect?Yes just land on the MLO lugs. MLO service panels aren't prohibited, just having more than one handle installed in them is. There is 230.62, but those don't have to be manufacturer provided.
So you can only supply one circuit with that method...never seen a temporary power panel with a single circuit.Yes just land on the MLO lugs. MLO service panels aren't prohibited, just having more than one handle installed in them is. There is 230.62, but those don't have to be manufacturer provided.
230.62(C) Barriers.
Barriers shall be placed in service equipment such that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
A double pole breaker serving a MWBC is the disconnect.Then what serves as a main disconnect?
A disconnect means ahead of the MLO panel?
2So you can only supply one circuit with that method..
A double pole breaker serving a MWBC is the disconnect.
A double pole breaker serving a MWBC is the disconnect.
Only 120V capability then with that method?
you could supply a larger single feeder and use the tap rules.Only 120V capability then with that method?
Seldom, if ever, need over 120V for a temp pole. The temp is just for workers to plug 120V equipment into, such as air compressors, saws, etc.Only 120V capability then with that method?
I have several contractors I do work for who use 240V 40/50 amp dehumidifier’s on site.Seldom, if ever, need over 120V for a temp pole. The temp is just for workers to plug 120V equipment into, such as air compressors, saws, etc.