wireman1
Senior Member
if the wires from a pad mounted trans. are in pipe and are buried 40 in .deepcan the 90 dregee column be usedto detrmine the ampicty of the wire.for instance a 500 mcm cable thwn is rated at430 amps . does it matter that the cables are buired under ground in determing which column in 310 .16 you can use especially if the cables are landed on a 75 degree terminal in which case the ampicty in the 75 degree column for a 500 mcm cable is 380 amps. being buried under ground does not have any exception on the cables amps?