Have a question pertaining to the temp column in the conductor amp rating tables. Now i know that thhn falls under the 90c column and have seen several references to using that temp. However i have always been told that you have to base it on the 75c column because thats the temp rating on most lugs. Now is this just having a complicated set of rules simplified to be safer than code for men in the field?
Sent from my SCH-I545 using Tapatalk
I agree that this is kind of confusing. But you have to remember that your components work together as a system, and you have to make sure you do not overheat the weakest link. Terminations on both sides of the wire, and then the wire itself, all in series, all subject to the same amperes, and all must be able to carry it safely.
In most practical situations, equipment is rated for 75C terminations. And this is true, even when the lugs are marked for AL9CU, or something similar that might indicate a 90C lug rating. The terminals on manufactured product are tested as a system with that manufactured product. And most of the time, manufactured product is only tested to allow for the 75C termination ratings. It is very rare that you have a situation where you can take advantage of a 90C lug rating.
For 100A and less, the official rule is that terminations are by default rated for 60C. This is mostly academic today, as most new equipment is listed and labeled otherwise for 75C.
This does make you wonder, what is the value of 90C wire, if I can't use the 90C column of the NEC?
Well, when you read the final sentence of NEC110.14(C), you'll see the most common reason why 90C wire has an advantage. The 90C column can be used for your conditions of use, temperature corrections and bundling ampacity adjustments. As long as the final ampacity is limited to the 75C value (without adjustments/corrections) when you terminate to equipment.
As an example, consider 4 current-carrying #6 conductors in a conduit 4" above the rooftop, in a place where the ambient is 33C.
4 CCC's in a raceway = 0.8 ampacity adjustment
4" above rooftop in direct sunlight = +17C temperature adder
Add that to 33C, and get 50C
50C for 90C rated wire = 0.82 temperature correction
Total correction factor = 0.82*0.8 = 0.656
Using 90C rated #6 Cu wire: 75A * 0.656 = 49.2A
Terminations at 75C are rated for 65A
Wire at conditions of use is rated for 49.2A
The ampacity of this circuit is thus rated for the smaller of the two, which is 49.2A