Scratch the paint of the can, then see aboveput a lug to the can
Im working on a temporary service and in need of some help. The disconnect has only one ground lug which is coming from my ground rods. Where does my ground to the panel come from? Any input would be appreciated.
Is the disconnect listed as "suitable for use as service equipment"? If so it will have provisions for the main bonding jumper and the required number of connections. If it is not so rated you can't use it for a service equipment and it will not have the main bonding jumper provision.