80 percent issue on T codes
80 percent issue on T codes
I appreciate everyone's comments, trying to have a sanity check and all the references are making me read the NEC closely once again. I did find the reference to 80% of AIT in article 501.125, I have the 2011 handbook and on page 748 in states the following:
"Totally enclosed motors of the types specified in article 500.125 (a)(2) or (a)(3) shall have no surface with an operating temperature in degrees Celsius in excess of 80 percent of the ignition temperature of the gas or vapor involved." The two mentioned references are talking about pressurized (purge) motors/enclosures and not to motors identified for Class I, Division 1 locations.
PS: I must have my head examined as I love this stuff, thanks again for all your comments.
If these are NRTL inspectors, they may be dealing with product standards which may be why they are citing ANSI/ISA.
The general NEC rule is Section 500.8(B)(1). Note is says nothing about 80% AIT as a general requirement. Also see Sections 500.8(D)(1) & (2).
There are some specific NEC rules in Section 501.15(A)(1)(1) and sprinkled in Article 501 Part III [starting in Section 501.100] that limit surface temperatures t0 80% AIT.
In general the 80 percent rule applies to Division 2 installations unless the equipment is suitable for Division 1.