When trying to determine allowable ampacity of Romex or UF cable do you have to use the 60 degree column? Thanks.
Yup I just found out about that recently . ThanksYes but you can use the 90C for de-rating. So basically after de-rating the rating of the wire cannot be used if larger than the 60C rating. The 60C column is the weak link.
For example, if after de-rating a conductor from the 90C column it is rated 50 amps but if the cable is rated 40 amps under the 60C column then the rating cannot be used higher than the 40 amps
You mean NM. Artical 334When trying to determine allowable ampacity of Romex or UF cable do you have to use the 60 degree column? Thanks.
Nice little interesting piece of information that was in my NFPA online NEC edition that I subscribe to.You mean NM. Artical 334
334.80
334.112
Informational note. The most common used is NM-B.
We call it Romex all the time as long as we know where to look.
Also review 334.116 Sheath.
Good info.
I believe NM-B came out in about 1984. Wasn't long after and all NM sheathed cable produced from then on was type NM-B. NEC eventually required it to be NM-B. Regular NM is still covered by code in order to deal with existing installations, but new installations are required to use NM-B.You mean NM. Artical 334
334.80
334.112
Informational note. The most common used is NM-B.
We call it Romex all the time as long as we know where to look.
Also review 334.116 Sheath.