I understand that the termination limitations in 110.14(C) are commonly understood to based on the table ampacity at the termination temperature rating without correction for ambient temperature. Two questions on that:
1) Is there any physics or listing reason that it is unnecessary to correct for temperature at the terminations? E.g. (to make up a possible explanation), that the UL listing for a piece of equipment would require it to be labeled with the allowable operating temperatures, and that the listing standard would confirm operation at the upper end of the allowable temperature range, where the conductors at the terminals are sized just by the table without temperature correction. Then the temperature effects at the terminals would be baked in already, with no need to do any further correction. Are any listing standards like that?
2) Code wise, what is the reading of 110.14(C) that supports this common understanding? (2017) 110.14(C)(1) says (second sentence): "Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.15(B)(16) as appropriately modified by 310.15(B)(7)." But Table 310.15(B)(16) is titled " . . . Based on Ambient Temperature of 30C" and has a footnote that says "*Refer to 310.15(B)(2) for the ampacity correction factors where the ambient temperature is other than 30°C (86°F)." So doesn't any reference to Table 310.15(B)(16) automatically include temperature correction per Table 310.15(B)(2) per the footnote?
Thank you,
Wayne
1) Is there any physics or listing reason that it is unnecessary to correct for temperature at the terminations? E.g. (to make up a possible explanation), that the UL listing for a piece of equipment would require it to be labeled with the allowable operating temperatures, and that the listing standard would confirm operation at the upper end of the allowable temperature range, where the conductors at the terminals are sized just by the table without temperature correction. Then the temperature effects at the terminals would be baked in already, with no need to do any further correction. Are any listing standards like that?
2) Code wise, what is the reading of 110.14(C) that supports this common understanding? (2017) 110.14(C)(1) says (second sentence): "Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.15(B)(16) as appropriately modified by 310.15(B)(7)." But Table 310.15(B)(16) is titled " . . . Based on Ambient Temperature of 30C" and has a footnote that says "*Refer to 310.15(B)(2) for the ampacity correction factors where the ambient temperature is other than 30°C (86°F)." So doesn't any reference to Table 310.15(B)(16) automatically include temperature correction per Table 310.15(B)(2) per the footnote?