viciousesque
Member
- Location
- california
- Occupation
- Electrician Trainee
Referencing NEC 2020
Can someone explain why a conductor in the 90C column of Table 310.16 gets corrected in Table 310.15(B)(1) even when the ambient temperature is below 90?
For example, 8 AWG THHN copper is rated at an ampacity of 55 amps in the 90C column. Why then do I need to apply temperature correction for temperatures BELOW 90?
I would think an ambient temperature of 90C would have an adjustment of 1.0.
Why do we apply temperature correction factors for ambient temperatures above 30C even for conductors with temperature ratings (from Table 310.16) well above 30C?
Thanks, all!
Can someone explain why a conductor in the 90C column of Table 310.16 gets corrected in Table 310.15(B)(1) even when the ambient temperature is below 90?
For example, 8 AWG THHN copper is rated at an ampacity of 55 amps in the 90C column. Why then do I need to apply temperature correction for temperatures BELOW 90?
I would think an ambient temperature of 90C would have an adjustment of 1.0.
Why do we apply temperature correction factors for ambient temperatures above 30C even for conductors with temperature ratings (from Table 310.16) well above 30C?
Thanks, all!