I have a question about derating conductors for ampacity versus temperature, art. 310.16.
My scenario takes place in a manufacturing facility. We have a 24 foot ceiling with 4 conduits running the length of the plant, 4 foot down from the ceiling, (paralleled feeders). Only 3 current carrying THHN conductors per conduit, 480v 3 phase Delta.
Although it?s warm inside the plant in the summer time, the other 3 out of 4 seasons inside the plant here in NJ are cool.
At what point does a person have to use temperature correction factors for conductors concerning ambient temperature?
In other words, how long does the temperature have to stay at a certain range and for how long or short a time before correction factors need to be applied?
Thanks.
My scenario takes place in a manufacturing facility. We have a 24 foot ceiling with 4 conduits running the length of the plant, 4 foot down from the ceiling, (paralleled feeders). Only 3 current carrying THHN conductors per conduit, 480v 3 phase Delta.
Although it?s warm inside the plant in the summer time, the other 3 out of 4 seasons inside the plant here in NJ are cool.
At what point does a person have to use temperature correction factors for conductors concerning ambient temperature?
In other words, how long does the temperature have to stay at a certain range and for how long or short a time before correction factors need to be applied?