we have a 8amp fuse in a control panel for a boiler that was blowing. the cause was determined as a short in the wires that lead to e-stops that were added to the system.
a continuity test and megger were used to determine there was no short in the wires. Now, the wires (2- 14awg thhn) run into a 3/4 conduit that passes directly under the boiler for about 8'. After removing these e-stops from the boiler, the fuse held.
-the temperature under the boiler is 300 degrees f.
-the length of conduit between controller and bottom of boiler is about 6'
should this wire have been de-rated due to this? and could this cause the fuse to blow.
thanks