Hi folks,
Long time reader, first time poster.
Couldn't resist.
First, thanks for all the helpful information you've posted throughout the years! This site really is amazing trove of knowledge.
Second, I'm trying to work through an ampacity derating of flexible cord under NEC 2008 Section 400.5 where the ambient temperature (Tma) is 50 C. I see from 400.5(A) the following:
As I flip over to Table 400.5(B), I learn that the caption is "Ampacity of Cable Types SC, SCE, SCT, PPE, G, G-GC, and W" ... which would be straight forward and make a lot of sense if I were to use one of those cable types.
Instead, I'm using SEOOW cord, which is covered under Table 400.5(A). Best as I've tried, I can't find any language in the NEC code that specifically relates temperature derating and Table 400.5(A).
So I'm hoping someone here can set me straight. A few direct questions:
Chris
Long time reader, first time poster.
First, thanks for all the helpful information you've posted throughout the years! This site really is amazing trove of knowledge.
Second, I'm trying to work through an ampacity derating of flexible cord under NEC 2008 Section 400.5 where the ambient temperature (Tma) is 50 C. I see from 400.5(A) the following:
Where cords are used in ambient temperatures exceeding 30 C, the temperature correction factors from Table 310.16 that correspond to the temperature rating of the cord shall be applied to the ampacity from Table 400.5(B).
As I flip over to Table 400.5(B), I learn that the caption is "Ampacity of Cable Types SC, SCE, SCT, PPE, G, G-GC, and W" ... which would be straight forward and make a lot of sense if I were to use one of those cable types.
Instead, I'm using SEOOW cord, which is covered under Table 400.5(A). Best as I've tried, I can't find any language in the NEC code that specifically relates temperature derating and Table 400.5(A).
So I'm hoping someone here can set me straight. A few direct questions:
- Is temperature derating on the values in Table 400.5(A) required?
- What is the relationship (if any exists) between Table 310.16 and Tables 400.5(A/B) when sizing a flexible cable?
Chris