Hello All,
Our project involves installing new electric heat trace on an existing outdoor pipeline that will be insulated with Rockwool and covered with metal covering and sealed to keep water out. This heated pipeline will occasionally pass through Class I Div. 2 areas.
Seeking confirmation regarding the temperature location needing to be evaluated that shall not exceed 80 percent of the autoignition temperature of the gas or vapor in the Class I Div. 2 Area.
I am attempting to resolve what appears to me to be a conflict between the NEC and ANSI/IEEE 515-2002. ANSI/IEEE 515-2002 is referenced in Article 427.1 Scope - Informational Note.
Is the temperature requiring evaluation taken from the exposed surface (outer surface of the insulated pipe covering) or from the sheath temperature on the pipe (under the covered insulation) of the pipe?
The sheath temperature is the temperature of the heating cables installed directly on the pipe and will be greater than the exposed surface temperature.
Per NEC:
Chapter 5 Special Occupancies - 501.135 Utilization Equipment.
(B) Class I, Division 2. In Class I, Division 2 locations, all utilization equipment shall comply with 501.135(B)(1) through (B)(3).
(1) Heaters. Electrically heated utilization equipment shall conform with either item (1) or item (2):
(1) The heater shall not exceed 80 percent of the autoignition temperature in degrees Celsius of the gas or vapor involved on any surface that is exposed to the gas or vapor when continuously energized at the maximum rated ambient temperature. If a temperature controller is not provided, these conditions shall apply when the heater is operated at 120 percent of rated voltage.
Per ANSI/IEEE 515-2002:
6.4.5 Hazardous (classified) locations
The resultant sheath temperature, Tsh, shall be less than the ignition temperature (°C) of the specific gas/vapor/dust involved,
Thank you in advance for any feedback you can provide to help clarify this issue.
Our project involves installing new electric heat trace on an existing outdoor pipeline that will be insulated with Rockwool and covered with metal covering and sealed to keep water out. This heated pipeline will occasionally pass through Class I Div. 2 areas.
Seeking confirmation regarding the temperature location needing to be evaluated that shall not exceed 80 percent of the autoignition temperature of the gas or vapor in the Class I Div. 2 Area.
I am attempting to resolve what appears to me to be a conflict between the NEC and ANSI/IEEE 515-2002. ANSI/IEEE 515-2002 is referenced in Article 427.1 Scope - Informational Note.
Is the temperature requiring evaluation taken from the exposed surface (outer surface of the insulated pipe covering) or from the sheath temperature on the pipe (under the covered insulation) of the pipe?
The sheath temperature is the temperature of the heating cables installed directly on the pipe and will be greater than the exposed surface temperature.
Per NEC:
Chapter 5 Special Occupancies - 501.135 Utilization Equipment.
(B) Class I, Division 2. In Class I, Division 2 locations, all utilization equipment shall comply with 501.135(B)(1) through (B)(3).
(1) Heaters. Electrically heated utilization equipment shall conform with either item (1) or item (2):
(1) The heater shall not exceed 80 percent of the autoignition temperature in degrees Celsius of the gas or vapor involved on any surface that is exposed to the gas or vapor when continuously energized at the maximum rated ambient temperature. If a temperature controller is not provided, these conditions shall apply when the heater is operated at 120 percent of rated voltage.
Per ANSI/IEEE 515-2002:
6.4.5 Hazardous (classified) locations
The resultant sheath temperature, Tsh, shall be less than the ignition temperature (°C) of the specific gas/vapor/dust involved,
Thank you in advance for any feedback you can provide to help clarify this issue.